RMS can be used to monitor particles. Whereas Rotronic doesn't offer particle counters, RMS allows for third party digital and analogue integration.
![](https://media-exp1.licdn.com/dms/image/C4E22AQEl4CWDVraimQ/feedshare-shrink_800-alternative/0?e=1605139200&v=beta&t=zgOMaVUC5t7rd-QXpEyv5GWkF2ppA7D5JqujInopBMM)
Digital devices (MODBUS TCP) can be integrated with the RMS-CONVERTER (https://www.rotronic.com/en-ch/rms-converter.html).
Analogue devices (0/4...20mA and 0...1/5/10V) can be integrated over LAN with the RMS-ADC-L-R (https://www.rotronic.com/en-ch/rms-adc-l-r.html) or wirelessly with the RMS-MADC-868/915-A/V (https://www.rotronic.com/en-ch/rms-m...ut-0-20ma.html).
Today, Rotronic AG have successfully integrated the following devices digitally:
1) Particle Measuring Systems Airnet II (https://www.pmeasuring.com/cas/produ...rticle-sensor/).
2) Lighthouse ApexR5 (https://www.golighthouse.com/en/airb...unters/apex-r5).
3) Climet Cl-3100 OPT Series (http://www.climet.com/products/ci3100_series.html).
The protocol files can be found here: https://service.rotronic.com/forum/f...modbus-library.
The following particle counters cannot be added to RMS digitally:
1) TSI, the MODBUS TCP protocol is not public (https://tsi.com/products/cleanroom-p...icle-counters/).
2) ParticlesPlus, the device requires a MODBUS TCP command to update the MODBUS addresses (https://particlesplus.com/).
Digital devices (MODBUS TCP) can be integrated with the RMS-CONVERTER (https://www.rotronic.com/en-ch/rms-converter.html).
Analogue devices (0/4...20mA and 0...1/5/10V) can be integrated over LAN with the RMS-ADC-L-R (https://www.rotronic.com/en-ch/rms-adc-l-r.html) or wirelessly with the RMS-MADC-868/915-A/V (https://www.rotronic.com/en-ch/rms-m...ut-0-20ma.html).
Today, Rotronic AG have successfully integrated the following devices digitally:
1) Particle Measuring Systems Airnet II (https://www.pmeasuring.com/cas/produ...rticle-sensor/).
2) Lighthouse ApexR5 (https://www.golighthouse.com/en/airb...unters/apex-r5).
3) Climet Cl-3100 OPT Series (http://www.climet.com/products/ci3100_series.html).
The protocol files can be found here: https://service.rotronic.com/forum/f...modbus-library.
The following particle counters cannot be added to RMS digitally:
1) TSI, the MODBUS TCP protocol is not public (https://tsi.com/products/cleanroom-p...icle-counters/).
2) ParticlesPlus, the device requires a MODBUS TCP command to update the MODBUS addresses (https://particlesplus.com/).