    Hi together,
    can anyone help me with a modbus problem I have with CRP5?
    I would like to read out the register 31001 (humidity value) and the length 2 registers (4 byte).
    But the value I get is not the humidity value.

  • #2
    Hi Theodor,

    To get the humidity value of the CRP5 please use the modbus address 31000 and not the modbus register address 31001.
    Everytime the modbus address is equal modbus register address -1 for CRP5.
    E. g.:
    - humidity: 31000, length 2
    - differential pressure: 31004, length 2
    - serial number CRP5: 30000, length 2

    See also Modbus manual https://www.rotronic.com/de-ch/produ...wnload?id=1084
    chapter 2.1 - see Attention!
    and
    see chapter 2.4.5 Example: Read Input Register

    Comment


    • #3
      See the instructions for use. Too good. Thank you!

      Comment


      • #4
        How I can return? The player is stumped, they can opt to skip or guess, unlocking more of the song heardle

        Comment


        • #5
          Originally posted by Werner Fürst View Post
          Hi Theodor,

          To get the humidity value of the CRP5 please use the modbus address 31000 and not the modbus register address 31001.
          Everytime the modbus address is equal modbus register address -1 for CRP5.
          E. g.:
          - humidity: 31000, length 2
          - differential pressure: 31004, length 2
          - serial number CRP5: 30000, length 2

          See also Modbus manual https://www.rotronic.com/de-ch/produ...wnload?id=1084melon sandbox
          chapter 2.1 - see Attention!
          and Melon Sandbox is the excellent choice for individuals who seek to engage with characters
          see chapter 2.4.5 Example: Read Input Register