Announcement

Collapse
No announcement yet.

FW Update RMS-MLOG-T

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • FW Update RMS-MLOG-T

    After a FW update from V1.1 to 1.2 a sensor error occured within my RMS Monitoring.
    Directly before the FW update there wasn't any error and the measurement value were displayed. The displayed temperature was app. 500°C.
    After the FW update, the RMS displayed a "--.--"
    Can anybody give me an idea about the reason?
    Last edited by Theodor K.; 21-03-2019, 13:08.

  • #2
    If the resistance of the external sensor approximates close to zero Ohm (depend on the sensor and the applied temperature - normally high temperatures), the device can misinterpret this as a short circuit. This is a new function of the RMS-MLOG V1.2.
    Solutions could be the use of another NTC sensor type with a higher resistance for the applied temperature range.

    Comment

    Working...
    X