Hi forum comunity,

is it possible to use barometric sensors to measure/calculate differential pressure? And is it possible within RMS?

Kind regards
Post #2 | 2019-10-21 11:06 UTC | James
Pretty easy to do, take 2 barometric pressure sensors and measure the difference between the two using a calculated measuring point within RMS.

Regards,
James
Post #3 | 2019-11-07 09:26 UTC | ME_Rotronic
Please consider, that the accuracy and the resolution of your barometric pressure sensor must fit your application. For example the RMS-MLOG-BT-915 sensor has an accuracy of +-3 hPa and a resolution of 0.1 hPa.
So for the MLOG-BT device you'd probably need a differential pressure of 200-500Pa.